Why is a flow rate on the water side required for heat exchangers?

2018-03-13 View Original

Thread Content

Why is there a maximum requirement for the flow rate on the water side of the heat exchanger?
Reply #2 2018-03-13
The recommended flow rate on the water side of the heat exchanger is 0.5~3 m/s
Reply #3 2018-03-13
The recommended flow rate on the water side of the heat exchanger is 0.9~3 m/s
Reply #4 2018-03-13
The Design Code for Industrial Circulating Cooling Water Treatment GB50050-2007 stipulates that the flow velocity in the cooling water pipeline should not be less than 0.9 m/s;
Reply #5 2018-03-14
The maximum flow rate is limited because high flow rates result in greater resistance, more noise, and an increased head pressure of the water pump

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.