During shutdown purging, how should flow meters and control valve assemblies be purged? I hope to receive guidance from all the teachers. Thank you!
Reply #22017-06-20
The control valve was removed and a bypass was created; the flow meter was also removed and a bypass was installed; the valve at the base of the pressure gauge was closed
Reply #32017-06-21
The flow meter and control valve should be removed and short-circuited
Reply #42017-06-22
The control valve can be disassembled and equipped with a baffle for purging via a bypass line; the mass flow meter must be removed. In cases where there is a bypass line, a fast-line is used, while in the absence of such a line, a short section is used as a substitute

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.