Slop tank arrangement

2017-10-09View Original

Thread Content

There is currently a 15-cubic-meter oil waste tank, connected directly to an oil removal tank (a larger tank) via a pipeline without any valves in between; the larger tank is equipped with a nitrogen seal. If the design pressure of the oil tank is at atmospheric pressure, is it not necessary to install emergency venting ports when considering fire scenarios? Are there any safety hazards?/ Or should the design pressure of the oil tank be increased?
Reply #22017-10-09
Firstly, it’s not very reasonable that the small and large containers didn’t have valves before; The nitrogen seal pressure generally does not exceed 2 kPa; a design pressure at atmospheric level is usually fine ; The emergency relief valve is primarily designed to prevent overpressure in the nitrogen seal; it has little to do with fires

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.