Hello everyone, what gauge should the main cable be for a total power consumption of 150 KW, using oxygen-free copper cables? Please upload the calculation formula, thank you.
Reply #22017-01-14
Transmission distance? Is it twenty meters or ten thousand meters?
Reply #32017-01-14
400 meters from the transformer to the electrical equipment
Reply #42017-01-15
400 meters is a bit far; it is recommended to use a single-strand copper wire with a diameter of 185, resulting in a voltage drop of around 20 volts
Reply #52017-01-15
I’m referring to motors with a power factor of 0.8; if it’s not a motor, 150 is more or less the same value. The key issue is whether you can accept the voltage drop
Reply #62017-01-15
Is it 150kw per unit, or are there several units, each with 150kw capacity? Does it handle capacitive loads, inductive loads, or resistive loads?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.