Lightning protection grounding and static electricity grounding

2017-05-10View Original

Thread Content

The cement foundation for the exhaust gas treatment facility covers an area of 5*13 meters, and it is used to house electrical equipment such as a 25-meter-high steel chimney and fans, as well as various pipelines. Can the lightning protection grounding for steel chimneys and the static protection grounding for equipment pipelines share the same grounding system? Also, is it necessary to embed flat steel around the foundation in advance for the static protection grounding of equipment pipelines?
Reply #22017-05-10
Is it embedded around the edges to facilitate device connections in various locations?
Reply #32017-05-11
Lightning protection grounding and anti-static grounding can share the same grounding network, but they must not share the same connection point. Special lightning protection devices such as lightning rods should be equipped with separate grounding wires and grounding piles

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.