There is currently a standalone power supply with a capacity of 500 KW and a voltage of 400 V. What is the maximum power of motors, centrifugal compressors, and reciprocating compressors that can be used with it? If a motor with a power of around 130 KW is used, can this issue be resolved by installing a soft starter?
Reply #22017-05-14
Experts, should this issue be reviewed?
Reply #32017-05-15
This requires calculating the starting voltage drop and the busbar-side voltage drop based on the characteristics of the equipment in order to determine it
Reply #42017-05-21
It depends on the length of the circuit and the cable selection; if the voltage drop is within acceptable limits, soft starting can be used to address the issue
Reply #52017-07-12
A 500KW generator with a 130KW motor for reduced-voltage starting should work fine; however, the other loads connected to the generator should not be too heavy. For specific calculations, refer to the section on diesel generator capacity calculation in “Matching Four”.
Reply #62017-07-15
Low-voltage starting is no problem; it mainly depends on whether you have any other loads
Reply #72017-07-19
Using reduced-voltage starting is no problem.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.