Thread Content
Should a semi-basement fire pump room of 60 square meters combined with a generator room of 36 square meters be classified as a Class C factory building? So according to Articles 3.7.2 and 3.7.6 of the Building Code GB50016-2014, are 2 enclosed stairwells required? OMG, is it designated as a civil building? Should it be classified as a public building? So, in addition to creating accessible restrooms, is energy-efficient design and registration also required? I don’t want to. I’m hoping experts can give me some advice. It was originally a little sparrow, but it has **troubles**.
The fire hazard can be determined based on the standards of the factory building.
My main question is: should two enclosed stairwells be built, or what is the appropriate approach? Thank you for your answer.
For the underground pump room, in accordance with clause 5.5.5, one evacuation staircase is sufficient
Clause 5.5.5 applies to civil buildings; this building is classified as a factory building. If it is designated as a civil building, it can only be a public building or a residential building, which is also not appropriate
It depends on whether your entire project is an industrial building or a regular residential one; in such cases it can be considered an auxiliary building, and since there’s no air conditioning system, there’s no need to worry about energy conservation