Seeking advice on explosion-proofing issues in areas where fuel gas is used in boiler combustion

2018-01-22View Original

Thread Content

As stated in the title, a small amount of fuel gas (with components of H2, CO, and CO2) is considered for use in CFB boilers; With a CO2 content of 96% v), what are the regulatory requirements for classifying areas as explosion-proof in the boiler area?
Reply #22018-02-14
There’s no need to draw explosion zones in the boiler room
Reply #32018-02-21
The boiler room shouldn’t be divided, but are there any leakage areas in the piping area?
Reply #42018-02-21
Are there valves on the pipeline (leak sources)? If not, there is no need to draw them. If there are: 1. In an area with good outdoor ventilation, no drawing is necessary. 2. In an indoor area with good ventilation and no open flames, it is Zone 2. 3. In an indoor area with poor ventilation and no open flames, it is Zone 1. All of the above are in accordance with Article 22 of Appendix B of GB50058-2014.
Reply #52023-09-19
Since the entire boiler room is located in a confined space, must it be classified as Zone 2 or Zone 1? Are there any distance range requirements?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.