In chemical plants, we consider restarting important motors; if there are many of them, they need to be restarted in batches. But how can we determine the impact of starting these motors together on the system? Is it the concern that the current will reach the tripping value for the incoming line, or is it the worry that the voltage will drop to the tripping value? What does so-called black start of the power grid mean?
Reply #22018-03-16
Calculate the voltage drop and current values of the motor group. First, the current must not exceed the quick-break value for incoming lines or the short-time overcurrent setting; second, it must not cause the contactors of the motors that have already started to trip again due to low control voltage!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.