Thread Content

Today, Schenk from the company said that the control power supply suddenly lost power. Upon on-site inspection, it was found that both the live wire and the neutral wire of the control power supply’s contactor were carrying electricity. A voltage measurement was taken using a multimeter on the live wire and neutral wire at the terminal block, but this caused the circuit to trip. Why does tripping occur when measuring voltage with the voltage range setting? I can guarantee there is no short circuit, as the live wire and the neutral wire are separated by several terminals. Later, after closing the circuit breaker, the power supply returned to normal. What’s going on here? Please help explain
Reply #22018-06-05
Since both the live wire and the neutral wire are charged, it indicates that the grounding of the neutral wire is poor, or the grounding of the panel/cabinet is inadequate; the tripping that occurs when measuring voltage is purely coincidental.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.