Recently, I observed the conditions of some fire hydrants in different locations and felt that there were more or less some issues. I’m posting this here; I’d appreciate it if friends could offer their opinions or suggestions regarding these fire hydrants. In particular, I’m interested in knowing what standards and regulations these opinions or suggestions are based on. For each diagram, those who provide a complete response first will receive high scores as a reward! See images on the floors below
Reply #22018-10-21
This post was last edited by ds66616 on 2018-10-21 21:44 – Status of short people
Reply #32018-10-21
Hidden among the grass baskets, this is barely visible; this one allows one to see above the head; this one is still fairly visible
Reply #42018-10-22
According to the specification book 01S201 \"Installation of Outdoor Fire Hydrants\", the installation height of this fire hydrant is insufficient, either due to a change in the ground level.
Reply #52018-10-22
According to the specifications in the 01S201 code \"Installation of Outdoor Fire Hydrants\", the distance from the center of these tall fire hydrant nozzles to the ground exceeds 450 mm, which may make it difficult to connect pipes to them.
Reply #62018-10-22
This post was last edited by “Hasty Passerby” on October 22, 2018, at 15:09. According to Article 7.2.6 of the “Technical Code for Fire Water Supply and Fire Hydrant Systems” GB 50974-2014, municipal fire hydrants shall be installed in locations such as sidewalks and green spaces where fire trucks can easily access them. They must not obstruct traffic, and must also comply with the following requirements: 1. The distance between a municipal fire hydrant and the roadside should be no less than 0.5 meters and no more than 2.0 meters; 3 Municipal fire hydrants should be avoided from being installed in locations prone to mechanical impact; if this is unavoidable, collision prevention measures must be taken. In the diagram, the two fire hydrants are one larger than 2.0m and the other smaller than 0.5m, with no collision protection measures.
Reply #72018-10-22
In my opinion, as long as it does not affect the water flow from the pipe connections, it is better to have fire hydrants that are shorter in height – this is due to considerations related to freezing in winter. In the catalogs, taller fire hydrants are prone to problems such as freezing and cracking during winter, with the exception of areas in the south where there is no snow.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.