This post was last edited by hesonchang214 on 2018-11-22 08:51. The maximum daily water demand in a certain city is 150,000 m3/day, with a time variation coefficient of 1.30. The water used by the water treatment plant itself accounts for 5%, and there are regulation tanks in the pipeline network; the maximum water supply rate to the pipeline network is 900 m3/h. What are the designed flow rates for the primary pump room and the secondary pump room? (Unit: m3/h) Solution: The designed flow rate for the primary pumping station is: 150000×(1+5%)/24 = 6562.5 m3/h. The designed flow rate for the secondary pumping station is: 150000/24×1.30 – 900 = 7225 m3/h
Reply #22018-11-22
6563m3/h, 7225m3/h
Reply #32018-11-22
6563m3/h; 7225m3/h
Reply #42018-11-22
6563m3/h, 7225m3/h
Reply #52018-11-22
The designed flow rate for the primary pumping station is: 150000×(1+5%)/24 = 6562.5 m3/h. The designed flow rate for the secondary pumping station is: 150000/24×1.30–900 = 7225 m3/h
Reply #62018-11-22
6563m3/h, 7225m3/h
Reply #72018-11-22
The maximum daily water demand in a certain city is 150,000 m3/day, with a time variation coefficient of 1.30. The water used by the water treatment plant itself accounts for 5%, and there are regulating tanks in the pipeline network; the maximum water supply rate to the pipeline network is 900 m3/h. What are the designed flow rates for the primary pump room and the secondary pump room?
Reply #82018-11-22
6562.5m3/h,7225m3/h
Reply #92018-11-22
Solution: The designed flow rate for the primary pumping station is: 150000×(1+5%)/24 = 6562.5 m3/h. The designed flow rate for the secondary pumping station is: 150000/24×1.30 – 900 = 7225 m3/h
Reply #102018-11-22
6563m3/h, 7225m3/h

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.