1. When the process system specifications or engineering design documents provide specific requirements for the design pressure of the vessel, the design pressure shall be determined in accordance with those specific requirements, but it shall not be lower than the values specified in the table. 2. The design pressure, together with the corresponding design temperature, shall be used as the design load conditions. Various operating conditions that the vessel may experience during operation must be taken into account, and the design pressure for the vessel under each such condition shall be determined accordingly. 3. The design pressure of containers holding liquefied gases shall comply with the following requirements: (1) In the absence of a safety relief device, the design pressure shall not be lower than 1.05 times the operating pressure; (2) When equipped with a safety valve, the design pressure shall not be lower than the set pressure of the safety valve (the set pressure is generally taken as 1.05 to 1.10 times the operating pressure); (3) The operating pressure refers to the saturated vapor pressure at the highest operating temperature that the container holding liquefied gases may reach. The working pressure of pressure vessels for storing liquefied gases or mixed liquefied petroleum gas at room temperature is determined in accordance with the current regulations, namely the \"Safety Technical Inspection Regulations for Fixed Pressure Vessels\" TSG21--2016. 4. For internal-pressure tower vessels that comply with the current industry standard \"Tower Vessels\" NB/T 47041, when the operating pressure is less than 0.1 MPa, the design pressure shall be set at not less than 0.1 MPa. 5. For vacuum vessels with an integral jacket, the calculated external pressure on the vessel shell shall equal the design external pressure plus the design internal pressure within the jacket, and the stability of the vessel shell under the jacket test pressure (external pressure) shall be verified. II. Principles for determining the design service life 1. The design service life is determined by the design agency based on the expected service life of the container. The expected service life of the container is specified in writing by the client who commissioned the design to the design firm. The design service life of pressure vessels shall be specified in the design drawings. 2. The design service life of pressure vessels is not identical to their actual service life. Users of pressure vessels shall conduct regular inspections and grading of the vessels in accordance with the requirements of the current regulations, namely the \"Safety Technical Inspection Regulations for Fixed Pressure Vessels\" TSG21-2016. When the operating conditions of the vessel change, the corrosion rate should be re-estimated based on actual measurement data to determine the vessel’s new service life. 3. When determining the design service life of a vessel, the following factors should be taken into account: (1) selection of appropriate materials and structural design; (2) reasonable corrosion allowance; (3) appropriate manufacturing and inspection requirements; (4) measures to limit creep (under high-temperature conditions) or fatigue; (5) cost of vessel construction; (6) role of the vessel in the plant; (7) operating cycle of the plant. 4. The design service life of containers shall comply with the following requirements: (1) For thick-walled hydrogenation reactors made of chromium-molybdenum steel or high-alloy steel with a nominal thickness of ≥50 mm: not less than 30 years; (2) For other reactors, columns with a diameter of ≥4 m, or a weight of ≥100 t, or a total height of ≥60 m, high-pressure heat exchanger shells, and containers with a nominal thickness of ≥50 mm, as well as spherical storage tanks: not less than 20 years; (3) For other columns, containers, heat exchanger shells, and tube banks: not less than 15 years. 5. For vessels with periodic variations in operating temperature or pressure, the number of cycles of such temperature or pressure changes during the design service life shall be specified in the design drawings.
Reply #22024-09-09
The principles for determining the design pressure are as follows: 1. If there are specific regulations, the design pressure shall be determined in accordance with those regulations, but it must not be lower than the minimum standard. 2. The design pressure must be determined based on the design temperature and possible operating conditions. 3. For containers used to hold liquefied gases, when there is no safety relief device, the design pressure shall be no less than 1.05 times the working pressure ; When a safety valve is installed, it shall not be lower than the set pressure of the safety valve. 4. The design pressure of internally pressurized tower-type vessels shall be no less than 0.1 MPa when the operating pressure is lower than this value. 5. For vacuum vessels with jackets, the design external pressure should be increased by the design internal pressure within the jacket; stability must also be checked. The principles for determining the design service life are as follows: 1. The design unit shall determine it based on the expected service life of the vessel, and this must be submitted in writing. 2. The design service life must be indicated in the drawings; it is different from the actual service life. 3. Factors such as material selection, corrosion margin, and manufacturing inspection requirements should be considered. 4. Minimum designed service life for specific types of containers: High-alloy reactors – not less than 30 years ; Large towers, high-pressure vessels, etc.: no less than 20 years ; Other towers, vessels, etc.: not less than 15 years. 5. For containers with periodically changing working conditions, the number of temperature or pressure cycles during the design service life shall be specified. .
Reply #32024-11-03
It should be specified in HG/T20580

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.