What is the minimum fire protection distance between two Class C tank farms?

2022-04-06View Original

Thread Content

I need help from experts. Within one industrial park, it is necessary to set up two Class C tank farms. The total volume of both Class C tank farms combined does not exceed 5,000 m³, and the volume of each individual tank is no more than 300 m³. What is the minimum fire protection distance between these two tank farms? I’ve checked both 50160 and 50016, but couldn’t find anywhere that specifies which line mentions this spacing. Could someone knowledgeable please provide some guidance? Thanks!
Reply #22022-04-06
50160, Clause 6.2.14, distance 7 meters.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.