Why is the equivalent length of a gate valve 8D, while that of a ball valve is 30D?

2017-06-07View Original

Thread Content

Generally, it is believed that ball valves have the lowest pressure drop. But why is the equivalent length of gate valves 8D, while that of ball valves is 30D? O(∩_∩)O Thank you
Reply #22017-06-07
It might be because of the different types of ball valves – there are two-piece types (with less resistance), and there are also one-piece types
Reply #32017-06-07
Logically, no matter what type of ball valve it is, when it is fully open, everything inside is fully connected
Reply #42017-06-07
I am working on the design of a roller kiln for daily-use porcelain, and I’m looking for some sample diagrams as reference. Email: 2730855438@qq.com
Reply #52017-06-08
The one of this type that is single-piece has a reduced diameter
Reply #62017-06-08
As stated in the book ”Flow of Fluids through Valves, Fittings, and Pipes“, the coefficient for gate valves (8fT) is greater than that for ball valves (3fT)
Reply #72017-06-08
Ball valves generally have reduced diameters on both sides of the ball, as full-bore ball valves are very expensive. Gate valves can be considered to have a full bore, so the resistance is low.
Reply #82017-06-08
It’s the first time I’ve heard of the concept of equivalent value; usually I just focus on buying and installing valves. It’s really interesting to learn about this
Reply #92017-06-08
OP, let me explain what length equivalent means. Also, you need to change your signature, haha.
Reply #102017-06-08
The equivalent length of a fitting is the length for which the local head loss caused by that fitting is equal to the frictional head loss incurred over a pipe of the same diameter over that same length; this length constitutes the equivalent length of the fitting
Reply #112017-06-08
Was it the editor who made a mistake due to blurred vision while entering 20570? .

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.