Which provision in the petrochemical regulations or building codes specifies the ventilation rate for Class A and Class B factories? ?

2017-08-01View Original

Thread Content

Which provision in the petrochemical regulations or building codes specifies the ventilation rate for Class A and Class B factories? ?
Reply #22017-08-02
The last edit to this post was made by Yangyang007 on 2017-8-2 at 09:31. Both GB50019-2014 and HGT20698-2009 deal with heating and ventilation; the Building Code and the Petrochemical Code only contain requirements related to the HVAC field. The specific number of air changes and the methods for calculation need to be determined in accordance with the relevant professional standards
Reply #32017-08-02
May I ask what specific professional standards they are? ?
Reply #42017-08-02
This post was last edited by Yangyang007 on 2017-8-2 at 14:16. According to clause 5.6.3 of HGT 20698-2009, \"the ventilation rate for emergency ventilation should be no less than 12 times per hour.\" Emergency ventilation is necessary in rooms where harmful gases or gases with explosion risks may be released suddenly in large quantities (typically referring to Class A and Class B factories, as well as areas containing toxic substances such as liquid chlorine and liquid ammonia). Appendix C mentions that specific requirements regarding the ventilation rate for production workshops handling certain substances are provided; the user can determine the appropriate value based on the substances handled in the production facility. Clause 6.4.3 of GB50019-2014 states that \"the ventilation rate for emergency ventilation should be no less than 12 times per hour, calculated based on the volume of the room.\" When considering ventilation, especially in hazardous areas, the highest possible ventilation rate should be adopted, and the appropriate equipment should be selected based on the calculated air volume

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.