May the fire-fighting water, as well as the water for production and daily use, share the same pipeline in a Class V warehouse of level 2?

2018-08-07View Original

Thread Content

In a Class V warehouse of level 2, are fire hydrants connected to the water supply network? Is that acceptable? The 2006 version of the building codes allowed for combined use, but this provision is no longer included in the current version
Reply #22018-08-09
Sure. However, after subtracting the water consumption for production and domestic use from the total flow in the water supply network, the remaining flow must meet the requirements for fire-fighting water use in Class E warehouses.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.