Is it necessary to install two level gauges on the methanol tank?

2017-06-05View Original

Thread Content

2 cubic meters methanol tank, at normal temperature and pressure. The tank is equipped with a flange, allowing the installation of a magnetic flip-level gauge. But the manager said they weren’t quite confident, so two needed to be installed. Is it necessary? If necessary, there is an opening on top of the tank; would a top-mounted magnetic flap level gauge be a suitable choice? Or would a float level gauge work?
Reply #22017-06-05
Sure, it prevents one problem, and there’s another as well
Reply #32017-06-05
You can install one on-site and one for remote transmission. That’s how it’s perfect
Reply #42017-06-05
One for local monitoring, where a magnetic flip switch can be used; one for remote monitoring, for which a guided-wave radar level gauge or a float level gauge can be chosen. After all, methanol is flammable, explosive, and toxic, so it’s better to have two sensors. It is recommended to use a radar gauge for remote monitoring, as if both sensors are of the float type, the decrease in density due to liquid expansion in high temperatures during summer could cause problems
Reply #52017-06-05
Can a float level gauge be installed by dropping it in from the top?
Reply #62017-06-05
The workshop is equipped with air conditioning. Could you recommend some manufacturers for float level gauges and magnetic flap level gauges?
Reply #72017-06-05
This is usually how we design it
Reply #82017-06-05
The two have higher security. It is best for the two level gauges to be of different types, such as one being a magnetic flip-type gauge and the other a radar gauge.
Reply #92017-06-05
It is recommended to install one on-site and one for remote transmission. This way, they can check each other.
Reply #102017-06-05
For a tank with a volume of 2 cubic units, one magnetic flip valve is sufficient.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.