How to configure the inverter to output the current signal to the DCS? Should the range setting be set to the motor’s rated current or to the instantaneous current?
Reply #22017-10-11
4-20MA, with the range set to the rated current.
Reply #32017-10-11
Work according to the rated current, and make it a bit larger.
Reply #42017-10-11
This is easy to understand; you can think of the frequency converter as a transmitter, as long as the range set in the DCS matches that set on the frequency converter
Reply #52017-10-11
I agree with the view above – the range is what it is, corresponding to the rated current in the frequency converter
Reply #62017-10-12
It’s been resolved, thank you all for your help. What I did was use a motor with a rated current of 160A; the frequency converter was able to increase the output by a factor of 1.75, so I set the value to 0–280A
Reply #72017-10-16
You say that if you treat the inverter as a transmitter, then it makes sense

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.