Regarding power supply for the PLC control cabinets in the workshop

2017-10-26View Original

Thread Content

The workshop requires a PLC power cable with a power rating of 4KW at 220V. It is necessary to supply power from the power cabinet in the control room’s cabinet area (via the UPS circuit). The length of the cable needed is around 210 meters; it should be installed in galvanized cable trays for instrumentation, and separated from signal cables by partitions. My question is: what size cable should I choose? Is the specification ZR-YJV-0.6/1KV 3×6 acceptable? How is the intermediate pressure drop loss calculated? It’s quite difficult to have the meter technician calculate these. Is there a manual available?
Reply #22017-10-26
At an operating temperature of 30°C, the current-carrying capacity under a continuous 90% load for a long period is as follows: 1.5 square millimeters – 18A; 2.5 square millimeters – 26A ; 4 square millimeters – 26A ; 6 square millimeters – 47A ; 10 square millimeters – 66A 16 square millimeters – 92A ; 25 square millimeters – 120A ; 35 square millimeters – 150A. Power P = Voltage U × Current I = 220 volts × 18 amps = 3960 watts. Values for the current load that wires can handle, as specified in standard GB4706.1-1992/1998 (partial list): For copper-wired cables: Cross-sectional area of the copper wire… Allowable continuous current: 2.5 square millimeters (16A–25A); 4 square millimeters (25A–32A); 6 square millimeters (32A–40A). For aluminum-wired cables: Cross-sectional area of the aluminum wire… Allowable continuous current: 2.5 square millimeters (13A–20A); 4 square millimeters (20A–25A); 6 square millimeters (25A–32A). The formula for calculating voltage drop in cables is ΔU = (P × L) / (A × S), where P represents the load on the circuit ; L is the length of the line ; A is the conductor material coefficient (around 77 for copper, around 46 for aluminum) ; S is the cross-sectional area of the cable.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.