How to understand the probe length Ln in E+H guided wave radar?

2017-10-27View Original

Thread Content

All of E+H’s guided wave radars have a parameter called probe length Ln. If this probe length is actually reduced, for example by truncating it, does it require corresponding adjustments to be made in the radar transmitter? What effects would occur if the empty mark is a bit lower than the full mark? For example, the empty mark is 16M and the full mark is 17M
Reply #22017-10-27
For antennas with waveguide rods or cables, if they are shortened, it is best to make a change in the configuration and enter the actual length. The cable length is the measurement range. The empty mark and the full mark should represent the range; empty is 16 and full is 17. Does that mean the range is 16–17?
Reply #32017-10-27
The ln length is not difficult to modify; the full scale corresponds to the maximum range, while the zero scale represents the full scale plus the dead zone. The value of ln can be greater than (full scale + dead zone), meaning that the zero level can be located in the middle of the guided wave tube. Please read the instructions carefully. Guiding waves tubes are generally used in horizontal tubes.
Reply #42017-10-27
Thank you. Will it cause any problems if I set the empty mark at 16m and the full mark at 17m?
Reply #52017-10-27
As long as ln is greater than 17, there’s no problem; the maximum distance is 17 meters below the flange
Reply #62017-10-27
As long as ln is greater than 17, there’s no problem; the maximum distance is 17 meters below the flange
Reply #72017-10-28
LN refers to the length of the probe; if it has a rod, that rod can be removed, and the parameters need to be adjusted accordingly. The one we purchased was 12 meters long, and after removing the rod its length becomes around 6 meters. It has been in use for a year now, but it often gives inaccurate readings when not in use
Reply #82017-10-28
Well, if this LN is shortened, does the configuration need to be adjusted accordingly?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.