UPS power supply

2018-01-07View Original

Thread Content

May I ask whether the SANTAK CASTLE 3C20KS(6G) UPS can start up when there is no mains power and no load connected?
Reply #22018-01-07
As long as the battery has sufficient charge, starting is no problem. How long the system time can be maintained depends on the capacity of your battery. Generally, it’s fine to leave it without a load for 2 hours.
Reply #32018-01-07
It can be started; with no load, it can run for a long time.
Reply #42018-01-08
Yes, it didn’t start even after a few attempts at startup; it shut down automatically each time. I don’t know why it was able to start today
Reply #52018-01-08
Did someone accidentally change the settings?
Reply #62018-01-08
This is possible, provided you know how much battery power remains. Saito models of 6KVA and above have two startup modes: startup using mains power and startup using direct current when there is no mains power (cold start)

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.