S7-300 diagnosis contents

2018-03-20View Original

Thread Content

The PLC system has been used for several years. Recently, it was running and entered a stop state. The SF light was on. I did an online diagnosis and the content is as follows.: Diagnostic buffer for module CPU 313C-2 DP Order number/Description Component version 6ES7 313-6CF03-0AB0 Hardware 2 - - - Firmware V 2.6.11 Boot Loader Firmware extension A 0.21.0 Rack: 0 slot: 2 serial number: S C-A2XL42932010 Event 24 / 100: Event ID 16# 38C4 Distributed I/0: The station returns the address of the affected DP slave.: Station number: 99 DP master system ID: 1 Logical base address of the DP slave: Enter address: 1023 Logical base address of the DP master: 1022 Required OB: Rack failure OB (OB86) In the current operating mode, the OB is not found, or is disabled, or cannot be started. External error, leaving event 23:49:06.477 2000-09-22 (Coding: 16# 38C4 FE56 C054 03FE 03FF 0163) Event 25 / 100: Event ID 16# 3842 Module determines the module type: Distributed I/0 input address: 1023 User information available Diagnostic interrupt from substitute OB required: Diagnostic interrupt OB (OB82) In the current operating mode, the OB was not found, or was disabled, or could not be started. External error, leaving event 23:49:06.418 2000-09-22 (coding: 16# 3842 FE52 C554 03FF 0063 0000) Event 26 / 100: Event ID 16# 39C4 Distributed I/0: Address of the DP slave affected by station failure: Station number: 99 DP master system ID: 1 Logical base address of the DP slave: Enter address: 1023 Logical base address of the DP master: 1022 Required OB: Rack failure OB (OB86) In the current operating mode, the OB is not found, or is disabled, or cannot be started. External error, incoming event 23:49:06.153 2000-09-22 (Coding: 16# 39C4 FE56 C054 03FE 03FF 0163) Event 27 / 100: Event ID 16# 38C4 Distributed I/0: The station returns the address of the affected DP slave.: Station number: 99 DP master system ID: 1 Logical base address of the DP slave: Enter address: 1023 Logical base address of the DP master: 1022 Required OB: Rack failure OB (OB86) In the current operating mode, the OB is not found, or is disabled, or cannot be started. External error, leaving event 23:49:06.122 2000-09-22 (Coding: 16# 38C4 FE56 C054 03FE 03FF 0163) Event 28 / 100: Event ID 16# 3842 Module determines the module type: Distributed I/0 input address: 1023 User information available Diagnostic interrupt from substitute OB required: Diagnostic interrupt OB (OB82) In the current operating mode, the OB was not found, or was disabled, or could not be started. External error, leaving event 23:49:06.048 2000-09-22 (coding: 16# 3842 FE52 C554 03FF 0063 0000) Event 29 / 100: Event ID 16# 39C4 Distributed I/0: Address of the DP slave affected by station failure: Station number: 99 DP master system ID: 1 Logical base address of the DP slave: Enter address: 1023 Logical base address of the DP master: 1022 Required OB: Rack failure OB (OB86) In the current operating mode, the OB is not found, or is disabled, or cannot be started. External error, incoming event 23:47:14.203 2000-09-22 (Coding: 16# 39C4 FE56 C054 03FE 03FF 0163) Event 30 / 100: Event ID 16# 38C4 Distributed I/0: The station returns the address of the affected DP slave.: Station number: 99 DP master system ID: 1 Logical base address of the DP slave: Enter address: 1023 Logical base address of the DP master: 1022 Required OB: Rack failure OB (OB86) In the current operating mode, the OB is not found, or is disabled, or cannot be started. External error, leaving event 23:47:12.092 2000-09-22 (Coding: 16# 38C4 FE56 C054 03FE 03FF 0163) Event 31 / 100: Event ID 16# 3842 Module determines the module type: Distributed I/0 input address: 1023 User information available Diagnostic interrupt from substitute OB required: Diagnostic interrupt OB (OB82) In the current operating mode, the OB was not found, or was disabled, or could not be started. External error, leaving event 23:47:12.024 2000-09-22 (coding: 16# 3842 FE52 C554 03FF 0063 0000) Event 32 / 100: Event ID 16# 39C4 Distributed I/0: Address of the DP slave affected by station failure: Station number: 99 DP master system ID: 1 Logical base address of the DP slave: Enter address: 1023 Logical base address of the DP master: 1022 Required OB: Rack failure OB (OB86) In the current operating mode, the OB is not found, or is disabled, or cannot be started. External error, incoming event 23:47:11.760 2000-09-22 (Coding: 16# 39C4 FE56 C054 03FE 03FF 0163) Event 33 / 100: Event ID 16# 38C4 Distributed I/0: The station returns the address of the affected DP slave.: Station number: 99 DP master system ID: 1 Logical base address of the DP slave: Enter address: 1023 Logical base address of the DP master: 1022 Required OB: Rack failure OB (OB86) In the current operating mode, the OB is not found, or is disabled, or cannot be started. External error, leaving event 23:47:11.728 2000-09-22 (Coding: 16# 38C4 FE56 C054 03FE 03FF 0163) Event 34 / 100: Event ID 16# 3842 Module determines the module type: Distributed I/0 input address: 1023 User information available Diagnostic interrupt from substitute OB required: Diagnostic interrupt OB (OB82) In the current operating mode, the OB was not found, or was disabled, or could not be started. External error, leaving event 23:47:11.654 2000-09-22 (coding: 16# 3842 FE52 C554 03FF 0063 0000) Event 35 / 100: Event ID 16# 39C4 Distributed I/0: Address of the DP slave affected by station failure: Station number: 99 DP master system ID: 1 Logical base address of the DP slave: Enter address: 1023 Logical base address of the DP master: 1022 Required OB: Rack failure OB (OB86) In the current operating mode, the OB is not found, or is disabled, or cannot be started. External error, incoming event 23:47:09.610 2000-09-22 (Coding: 16# 39C4 FE56 C054 03FE 03FF 0163) Event 36 / 100: Event ID 16# 4303 Operating mode before STOP mode caused by activating the stop switch: RUN request working mode: STOP (internal) Incoming event 23:43:00.852 2000-09-22 (Coding: 16# 4303 FF84 0000 0000 0000 0000) Event 37 / 100: Event ID 16# 4302 Mode switched from STARTUP to RUN Startup information: - Timestamp time of last standby power-up - Current/last boot type for single processor operation: - Auto-warm restart admissibility for certain boot types after standby power-up: - Allow manual warm restart - Allow automatic warm restart The last valid operation or setting of the automatic start type on power-up: - After backup power-up, the operating mode before automatic warm restart: STARTUP (warm restart) requested operating mode: RUN entry event 23:39:37.911 2000-09-22 (Coding: 16# 4302 FF68 C700 0000 0810 7710) Event 38 / 100: Event ID 16# 1382 Request automatic warm start STOP Reason: Power failure boot information: - Boot without modified system configuration - No difference between default and actual configuration - Timestamp time of last standby power-up - Single processor operation Current/last boot type: - Automatic warm restart after standby power-up Admissibility of certain boot types: - Allow Manual Warm Start - Allow automatic warm restart on power up The last valid operation or setting of the automatic start type: - OBs required for automatic warm restart after standby power up: Start OB (OB100) priority level: 27 Incoming event 23:39:37.909 2000-09-22 (Coding: 16# 1382 1B64 C772 494E 0810 7710) Event 39 / 100: Event ID 16# 4301 Mode switching from STOP to STARTUP STOP Reason: Power failure startup information: - Timestamp time of last standby power-up - Current/last boot type for single processor operation: - Auto-warm restart admissibility for certain boot types after standby power-up: - Allow manual warm restart - Allow automatic warm restart The last valid operation or setting of the automatic start type on power-up: - After backup power-up, the operating mode before automatic warm restart: STOP (internal) Requested operating mode: STARTUP (warm start) Incoming event 23:39:37.310 2000-09-22 (Coding: 16# 4301 FF46 C772 494E 0810 7710) Event 40 / 100: Event ID 16# 38C4 Distributed I/0: The station returns the address of the affected DP slave.: Station number: 99 DP master system ID: 1 Logical base address of the DP slave: Enter address: 1023 Logical base address of the DP master: 1022 Required OB: Rack failure OB (OB86) In the current operating mode, the OB is not found, or is disabled, or cannot be started. External error, leaving event 23:39:36.912 2000-09-22 (Coding: 16# 38C4 FE56 C054 03FE 03FF 0163) Event 41 / 100: Event ID 16# 3842 Module determines the module type: Distributed I/0 input address: 1023 User information available Diagnostic interrupt from substitute OB required: Diagnostic interrupt OB (OB82) In the current operating mode, the OB was not found, or was disabled, or could not be started. External error, leaving event 23:39:36.836 2000-09-22 (coding: 16# 3842 FE52 C554 03FF 0063 0000) Event 42 / 100: Event ID 16# 5371 Distributed I/0: End of synchronization of the number of distributed stations with the DP master/IO controller on slot 2: 1 Incoming event 23:39:36.827 2000-09-22 (Coding: 16# 5371 FF02 C150 0001 0000 0000) Event 43 / 100: Event ID 16# 4300 Working mode before backup power on: Operating mode without voltage request: STOP (self-initialized) Incoming event 23:39:32.958 2000-09-22 (Coding: 16# 4300 FFF3 0000 0000 0000 0000) Event 44 / 100: Event ID 16# 494E Operating mode before power failure: RUN request working mode: No voltage external error, incoming event 23:39:13.461 2000-09-22 (Coding: 16# 494E FF8F C000 0000 0000 0000) Event 45 / 100: Event ID 16# 4302 Mode switch from STARTUP to RUN Startup information: - Timestamp time of last standby power-up - Single processor operation Current/last boot type: - Warm boot triggered by switch setting ; Last power-on was in standby mode. Permissibility for certain startup types: – Manual warm start is allowed – Automatic warm start is allowed. Last valid operation or setting for the automatic startup type at power-on: – Warm start is triggered via switch setting ; Last power-on was in standby mode. Previous operating mode: STARTUP (warm start). Requested operating mode: RUN. Event occurred at 08:27:46.068 on 2000-09-22 (encoding: 16# 4302 FF68 C700 0000 0813 7713). Event 46/100: Event ID 16# 1381 – request for manual warm start. STOP reason: STOP mode triggered by activation of the stop switch. Startup information: – Startup is carried out without using the modified system configuration; there is no difference between the preset configuration and the actual configuration. – Time stamp of the last standby power-on. – Single-processor operation: Warm start is triggered via switch settings ; Last power-on was in standby mode. Permissibility for certain startup types: – Manual warm start is allowed – Automatic warm start is allowed. Last valid operation or setting for the automatic startup type at power-on: – Warm start is triggered via switch setting ; Last power-on was in standby mode. Required OB: Startup OB (OB100). Priority level: 27. Event occurrence time: 08:27:46.066, 2000-09-22 (Encoding: 16# 1381 1B64 C772 4303 0813 7713). Event 47/100: Event ID 16# 4301; mode changed from STOP to STARTUP. Reason for STOP: Activation of the stop switch led to STOP mode. Startup information: – Timestamp of the last standby power-on; – Single-processor operation. Current/past startup type: – Warm start triggered by switch setting ; Last power-on was in standby mode. Permissibility for certain startup types: – Manual warm start is allowed – Automatic warm start is allowed. Last valid operation or setting for the automatic startup type at power-on: – Warm start is triggered via switch setting ; Last power-on was in standby mode. Previous operating mode: STOP (internal). Requested operating mode: STARTUP (warm start). Event occurred at 08:27:45.469 on 2000-09-22 (encoding: 16# 4301 FF46 C772 4303 0813 7713). Event 48/100: Event ID 16# 4303 – activation of the stop switch led to STOP mode. Previous operating mode: RUN. Requested operating mode: STOP (internal). Event occurred at 08:24:05.524 on 2000-09-22 (encoding: 16# 4303 FF84 0000 0000 0000 0000). Event 49/100: Event ID 16# 4302 – mode changed from STARTUP to RUN. Startup information: – Time stamp of the last standby power-on; single-processor operation. Current/past startup type: – Warm start triggered by switch setting ; Last power-on was in standby mode. Permissibility for certain startup types: – Manual warm start is allowed – Automatic warm start is allowed. Last valid operation or setting for the automatic startup type at power-on: – Warm start is triggered via switch setting ; Last power-on was in standby mode. Previous operating mode: STARTUP (warm start). Requested operating mode: RUN. Event occurred at 08:21:17.268 on 2000-09-22 (encoding: 16# 4302 FF68 C700 0000 0813 7713). Event 50/100: Event ID 16# 1381; request for manual warm start. STOP reason: STOP mode triggered by activation of the stop switch. Startup information: – Started without using the modified system configuration – No difference between the preset configuration and the actual configuration – Timestamp of the last standby power-on. Single-processor operation: – Warm start triggered via switch setting ; Last power-on was in standby mode. Permissibility for certain startup types: – Manual warm start is allowed – Automatic warm start is allowed. Last valid operation or setting for the automatic startup type at power-on: – Warm start is triggered via switch setting ; Last power-on was in standby mode. Required OB: Startup OB (OB100). Priority level: 27. Event occurrence time: 08:21:17.266, 2000-09-22 (Encoding: 16# 1381 1B64 C772 4303 0813 7713). Event 51/100: Event ID 16# 4301; mode changed from STOP to STARTUP. Reason for STOP: Activation of the stop switch led to STOP mode. Startup information: – Time stamp of the last standby power-on; single-processor operation. Current/past startup type: – Warm start triggered by switch setting ; Last power-on was in standby mode. Permissibility for certain startup types: – Manual warm start is allowed – Automatic warm start is allowed. Last valid operation or setting for the automatic startup type at power-on: – Warm start is triggered via switch setting ; Last power-on was in standby mode. Previous operating mode: STOP (internal). Requested operating mode: STARTUP (warm start). Event occurred at 08:21:16.668 on 2000-09-22 (encoding: 16# 4301 FF46 C772 4303 0813 7713). Event 52/100: Event ID 16# 4303 – activation of the stop switch led to STOP mode. Previous operating mode: RUN. Requested operating mode: STOP (internal). Event occurred at 08:17:55.054 on 2000-09-22 (encoding: 16# 4303 FF84 0000 0000 0000 0000). Event 53/100: Event ID 16# 4302 – mode changed from STARTUP to RUN. Startup information: – Time stamp of the last standby power-on; single-processor operation. Current/past startup type: – Warm start triggered by switch setting ; Last power-on was in standby mode. Permissibility for certain startup types: – Manual warm start is allowed – Automatic warm start is allowed. Last valid operation or setting for the automatic startup type at power-on: – Warm start is triggered via switch setting ; Last power-on was in standby mode. Previous operating mode: STARTUP (warm start). Requested operating mode: RUN. Event occurred at 08:15:16.269 on 2000-09-22 (encoding: 16# 4302 FF68 C700 0000 0813 7713). Event 54/100: Event ID 16# 1381 – request for manual warm start. STOP reason: STOP mode triggered by activation of the stop switch. Startup information: – Startup is carried out without using the modified system configuration; there is no difference between the preset configuration and the actual configuration. – Time stamp of the last standby power-on. – Single-processor operation: Warm start is triggered via switch settings ; Last power-on was in standby mode. Permissibility for certain startup types: – Manual warm start is allowed – Automatic warm start is allowed. Last valid operation or setting for the automatic startup type at power-on: – Warm start is triggered via switch setting ; Last power-on was in standby mode. Required OB: Startup OB (OB100). Priority level: 27. Event occurrence time: 08:15:16.266, 2000-09-22 (Encoding: 16# 1381 1B64 C772 4303 0813 7713). Event 55/100: Event ID 16# 4301; mode changed from STOP to STARTUP. Reason for STOP: Activation of the stop switch led to STOP mode. Startup information: – Time stamp of the last standby power-on; single-processor operation. Current/past startup type: – Warm start triggered by switch setting ; Last power-on was in standby mode. Permissibility for certain startup types: – Manual warm start is allowed – Automatic warm start is allowed. Last valid operation or setting for the automatic startup type at power-on: – Warm start is triggered via switch setting ; Last power-on was in standby mode. Previous operating mode: STOP (internal). Requested operating mode: STARTUP (warm start). Event occurred at 08:15:15.669 on 2000-09-22 (encoding: 16# 4301 FF46 C772 4303 0813 7713). Event 56/100: Event ID 16# 4303 – activation of the stop switch led to STOP mode. Previous operating mode: RUN. Requested operating mode: STOP (internal). Event occurred at 08:03:41.694 on 2000-09-22 (encoding: 16# 4303 FF84 0000 0000 0000 0000). Event 57/100: Event ID 16# 4302 – mode switched from STARTUP to RUN. Startup information: – Time stamp of the last standby power-on; single-processor operation. Current/past startup type: – Warm start triggered by switch setting ; Last power-on was in standby mode. Permissibility for certain startup types: – Manual warm start is allowed – Automatic warm start is allowed. Last valid operation or setting for the automatic startup type at power-on: – Warm start is triggered via switch setting ; Last power-on was in standby mode. Previous operating mode: STARTUP (warm start). Requested operating mode: RUN. Event occurred at 07:57:16.871 on 2000-09-22 (encoding: 16# 4302 FF68 C700 0000 0813 7713). Event 58/100: Event ID 16# 1381 – request for manual warm start. STOP reason: STOP mode triggered by activation of the stop switch. Startup information: – Started without using the modified system configuration – No difference between the preset configuration and the actual configuration – Timestamp of the last standby power-on. Operation mode: – Warm start triggered via switch setting ; Last power-on was in standby mode. Permissibility for certain startup types: – Manual warm start is allowed – Automatic warm start is allowed. Last valid operation or setting for the automatic startup type at power-on: – Warm start is triggered via switch setting ; Last power-on was in standby mode. Required OB: Startup OB (OB100). Priority level: 27. Event occurrence time: 07:57:16.869, 2000-09-22 (Encoding: 16# 1381 1B64 C772 4303 0813 7713). Event 59/100: Event ID 16# 4301; mode changed from STOP to STARTUP. Reason for STOP: Activation of the stop switch led to STOP mode. Startup information: – Timestamp of the last standby power-on; single-processor operation. Current/past startup type: – Warm start triggered by switch setting ; Last power-on was in standby mode. Permissibility for certain startup types: – Manual warm start is allowed – Automatic warm start is allowed. Last valid operation or setting for the automatic startup type at power-on: – Warm start is triggered via switch setting ; Last power-on was in standby mode. Previous operating mode: STOP (internal). Requested operating mode: STARTUP (warm start). Event occurred at 07:57:16.271 on 2000-09-22 (encoding: 16# 4301 FF46 C772 4303 0813 7713). Event 60/100: Event ID 16# 4303 – activation of the stop switch led to STOP mode. Previous operating mode: RUN. Requested operating mode: STOP (internal). Event occurred at 06:50:59.924 on 2000-09-22 (encoding: 16# 4303 FF84 0000 0000 0000 0000). Event 61/100: Event ID 16# 4302 – mode changed from STARTUP to RUN. Startup information: – Time stamp of the last standby power-on; single-processor operation. Current/past startup type: – Warm start triggered by switch setting ; Last power-on was in standby mode. Permissibility for certain startup types: – Manual warm start is allowed – Automatic warm start is allowed. Last valid operation or setting for the automatic startup type at power-on: – Warm start is triggered via switch setting ; Last power-on was in standby mode. Previous operating mode: STARTUP (warm start). Requested operating mode: RUN. Event occurred at 01:09:51.070 on 2000-09-22 (encoding: 16# 4302 FF68 C700 0000 0813 7713). Event 62/100: Event ID 16# 1381 – request for manual warm start. STOP reason: STOP mode triggered by activation of the stop switch. Startup information: – Startup was carried out without using the modified system configuration; there is no difference between the preset configuration and the actual configuration. – Time stamp of the last standby power-on. – Single-processor operation: Warm start was triggered via switch settings ; Last power-on was in standby mode. Permissibility for certain startup types: – Manual warm start is allowed – Automatic warm start is allowed. Last valid operation or setting for the automatic startup type at power-on: – Warm start is triggered via switch setting ; Last power-on was in standby mode. Required OB: Startup OB (OB100). Priority level: 27. Event occurrence time: 01:09:51.068, 2000-09-22 (Encoding: 16# 1381 1B64 C772 4303 0813 7713). Event 63/100: Event ID 16# 4301; mode changed from STOP to STARTUP. Reason for STOP: Activation of the stop switch led to STOP mode. Startup information: – Time stamp of the last standby power-on; single-processor operation. Current/last startup type: Warm start triggered by switch setting ; Last power-on was in standby mode. Permissibility for certain startup types: – Manual warm start is allowed – Automatic warm start is allowed. Last valid operation or setting for the automatic startup type at power-on: – Warm start is triggered via switch setting ; Last power-up was in standby mode. Previous operating mode: STOP (internal). Requested operating mode: STARTUP (warm start). Event occurred at 01:09:50.472 on 2000-09-22. (Code: 16# 4301 FF46 C772 4303 0813 7713) Event 64 / 100: Event ID 16# 4303 – Activating the stop switch resulted in STOP mode. Previous operating mode: RUN. Requested operating mode: STOP (internal). Event occurred at 01:09:31.334 on 2000-09-22. (Code: 16# 4303 FF84 0000 0000 0000 0000) Event 65 / 100: Event ID 16# 4302 – Mode switched from STARTUP to RUN. Startup information: – Timestamp of the last standby power-up; single-processor operation. Current/last startup type: Automatic warm start after standby power-up. Permissible startup types: Manual warm start and automatic warm start are allowed. Last valid action/setting for automatic startup upon power-up: Automatic warm start after standby power-up. Previous operating mode: STARTUP (warm start). Requested operating mode: RUN. Event occurred at 01:08:20.793 on 2000-09-22. (Code: 16# 4302 FF68 C700 0000 0810 7710) Event 66 / 100: Event ID 16# 1382 – Automatic warm start requested. Reason for STOP: Power failure. Startup information: – System configuration was not modified during startup; no differences between preset and actual configurations; timestamp of the last standby power-up; single-processor operation. Current/last startup type: Automatic warm start after standby power-up. Permissible startup types: Manual warm start and automatic warm start are allowed. Last valid action/setting for automatic startup upon power-up: Automatic warm start after standby power-up. Required OB: Startup OB (OB100). Priority level: 27. Event occurred at 01:08:20.791 on 2000-09-22. (Code: 16# 1382 1B64 C772 494E 0810 7710) Event 67 / 100: Event ID 16# 4301 – Mode switched from STOP to STARTUP. Reason for STOP: Power failure. Startup information: Timestamp of the last standby power-up; single-processor operation. Current/last startup type: Automatic warm start after standby power-up. Permissible startup types: Manual warm start and automatic warm start are allowed. Last valid action/setting for automatic startup upon power-up: Automatic warm start after standby power-up. Previous operating mode: STOP (internal). Requested operating mode: STARTUP (warm start). Event occurred at 01:08:20.192 on 2000-09-22. (Code: 16# 4301 FF46 C772 494E 0810 7710) Event 68 / 100: Event ID 16# 38C4 – Distributed I/O: Station returned. Address of affected DP slave: Station number: 99. DP master system ID: 1. Logical base address for DP slave: Input address: 1023. Logical base address for DP master: 1022. Required OB: Rack fault OB (OB86). Under current operating mode, this OB cannot be found, is disabled, or cannot be started. External error; event ended at 01:08:19.794 on 2000-09-22. (Code: 16# 38C4 FE56 C054 03FE 03FF 0163) Event 69 / 100: Event ID 16# 3842 – Module identified. Module type: Distributed I/O. Input address: 1023. User information is available. Diagnostic interrupt from a substitute module. Required OB: Diagnostic interrupt OB (OB82). Under current operating mode, this OB cannot be found, is disabled, or cannot be started. External error; event ended at 01:08:19.718 on 2000-09-22. (Code: 16# 3842 FE52 C554 03FF 0063 0000) Event 70 / 100: Event ID 16# 5371 – Distributed I/O: Synchronization with DP master/IO controller on slot 2 completed. Number of distributed stations: 1. Event occurred at 01:08:19.709 on 2000-09-22. (Code: 16# 5371 FF02 C150 0001 0000 0000) Event 71 / 100: Event ID 16# 4300 – Standby power-up. Previous operating mode: No voltage. Requested operating mode: STOP (self-initialization). Event occurred at 01:08:15.840 on 2000-09-22. (Code: 16# 4300 FFF3 0000 0000 0000 0000) Event 72 / 100: Event ID 16# 494E – Power failure. Previous operating mode: RUN. Requested operating mode: No voltage. External error; event occurred at 01:08:07.338 on 2000-09-22. (Code: 16# 494E FF8F C000 0000 0000 0000) Event 73 / 100: Event ID 16# 4302 – Mode switched from STARTUP to RUN. Startup information: Timestamp of the last standby power-up; single-processor operation. Current/last startup type: Warm start triggered via switch settings ; Last power-on was in standby mode. Permissibility for certain startup types: – Manual warm start is allowed – Automatic warm start is allowed. Last valid operation or setting for the automatic startup type at power-on: – Warm start is triggered via switch setting ; Last power-on was in standby mode. Previous operating mode: STARTUP (warm start). Requested operating mode: RUN. Event occurred at 01:07:08.765 on 2000-09-22 (encoding: 16# 4302 FF68 C700 0000 0813 7713). Event 74/100: Event ID 16# 1381 – request for manual warm start. STOP reason: STOP mode triggered by activation of the stop switch. Startup information: – Started without using the modified system configuration; no difference between the preset and actual configurations. – Timestamp of the last standby power-on. – Single-processor operation: Warm start triggered via switch setting ; Last power-on was in standby mode. Permissibility for certain startup types: – Manual warm start is allowed – Automatic warm start is allowed. Last valid operation or setting for the automatic startup type at power-on: – Warm start is triggered via switch setting ; Last power-on was in standby mode. Required OB: Startup OB (OB100). Priority level: 27. Event occurrence time: 01:07:08.763, 2000-09-22 (Encoding: 16# 1381 1B64 C772 4303 0813 7713). Event 75/100: Event ID 16# 4301; mode changed from STOP to STARTUP. Reason for STOP: Activation of the stop switch led to STOP mode. Startup information: – Time stamp of the last standby power-on; single-processor operation. Current/past startup type: – Warm start triggered by switch setting ; Last power-on was in standby mode. Permissibility for certain startup types: – Manual warm start is allowed – Automatic warm start is allowed. Last valid operation or setting for the automatic startup type at power-on: – Warm start is triggered via switch setting ; The working mode before the last power-on was backup: STOP (internal) Requested operating mode: STARTUP (warm restart) Incoming event 01:07:08.166 2000-09-22 (Coding: 16# 4301 FF46 C772 4303 0813 7713) Event 76 / 100: Event ID 16# 4303 Activating the stop switch leading to the operating mode before STOP mode: RUN request working mode: STOP (internal) Incoming event 01:06:55.269 2000-09-22 (Coding: 16# 4303 FF84 0000 0000 0000 0000) Event 77 / 100: Event ID 16# 4302 Mode switched from STARTUP to RUN Startup information: - Timestamp time of last standby power-up - Current/last boot type for single processor operation: - Auto-warm restart admissibility for certain boot types after standby power-up: - Allow manual warm restart - Allow automatic warm restart The last valid operation or setting of the automatic start type on power-up: - After backup power-up, the operating mode before automatic warm restart: STARTUP (warm restart) requested operating mode: RUN entry event 23:40:33.529 2000-09-21 (Coding: 16# 4302 FF68 C700 0000 0810 7710) Event 78 / 100: Event ID 16# 1382 Request automatic warm start STOP Reason: STOP due to I/O management Boot information: - Boot without modified system configuration - No difference between default and actual configuration - Time stamp of last standby power-up - Single processor operation Current/last boot type: - Automatic warm restart after standby power-up Admissibility of certain boot types: - Allow Manual Warm Start - Allow automatic warm restart on power up The last valid operation or setting of the automatic start type: - OBs required for automatic warm restart after standby power up: Start OB (OB100) priority level: 27 Incoming events 23:40:33.527 2000-09-21 (Coding: 16# 1382 1B64 C772 4548 0810 7710) Event 79 / 100: Event ID 16# 4301 Mode switching from STOP to STARTUP STOP Reason: Startup information entering STOP mode due to I/O management: - Timestamp time of last standby power-up - Current/last boot type for single processor operation: - Auto-warm restart admissibility for certain boot types after standby power-up: - Allow manual warm restart - Allow automatic warm restart The last valid operation or setting of the automatic start type on power-up: - After backup power-up, the operating mode before automatic warm restart: STOP (internal) Requested operating mode: STARTUP (warm start) Incoming event 23:40:32.928 2000-09-21 (Coding: 16# 4301 FF46 C772 4548 0810 7710) Event 80 / 100: Event ID 16# 38C4 Distributed I/0: The station returns the address of the affected DP slave.: Station number: 99 DP master system ID: 1 Logical base address of the DP slave: Enter address: 1023 Logical base address of the DP master: 1022 Required OB: Rack failure OB (OB86) In the current operating mode, the OB is not found, or is disabled, or cannot be started. External error, leaving event 23:40:32.530 2000-09-21 (Coding: 16# 38C4 FE56 C054 03FE 03FF 0163) Event 81 / 100: Event ID 16# 3842 Module determines the module type: Distributed I/0 input address: 1023 User information available Diagnostic interrupt from substitute OB required: Diagnostic interrupt OB (OB82) In the current operating mode, the OB was not found, or was disabled, or could not be started. External error, leaving event 23:40:32.454 2000-09-21 (coding: 16# 3842 FE52 C554 03FF 0063 0000) Event 82 / 100: Event ID 16# 5371 Distributed I/0: End of synchronization of the number of distributed stations with the DP master/IO controller on slot 2: 1 Incoming event 23:40:32.445 2000-09-21 (Coding: 16# 5371 FF02 C150 0001 0000 0000) Event 83 / 100: Event ID 16# 4300 Working mode before backup power on: Operating mode without voltage request: STOP (self-initialized) Incoming event 23:40:28.576 2000-09-21 (Coding: 16# 4300 FFF3 0000 0000 0000 0000) Event 84 / 100: Event ID 16# 494E Operating mode before power failure: STOP (internal) Requested operating mode: No voltage external error, incoming event 23:40:14.060 2000-09-21 (Coding: 16# 494E FF4F C000 0000 8005 0000) Event 85 / 100: Event ID 16# 39C4 Distributed I/0: Address of the DP slave affected by station failure: Station number: 99 DP master system ID: 1 Logical base address of the DP slave: Enter address: 1023 Logical base address of the DP master: 1022 Required OB: Rack failure OB (OB86) In the current operating mode, the OB is not found, or is disabled, or cannot be started. External error, incoming event 23:40:13.424 2000-09-21 (Coding: 16# 39C4 FE56 C054 03FE 03FF 0163) Event 86 / 100: Event ID 16# 38C4 Distributed I/0: The station returns the address of the affected DP slave.: Station number: 99 DP master system ID: 1 Logical base address of the DP slave: Enter address: 1023 Logical base address of the DP master: 1022 Required OB: Rack failure OB (OB86) In the current operating mode, the OB was not found, or was disabled, or could not be started. External error, leaving event 23:32:53.348 2000-09-21 (Coding: 16# 38C4 FE56 C054 03FE 03FF 0163) Event 87 / 100: Event ID 16# 3842 Module determines the module type: Distributed I/0 input address: 1023 User information available Diagnostic interrupt from substitute OB required: Diagnostic interrupt OB (OB82) In the current operating mode, the OB was not found, or was disabled, or could not be started. External error, leaving event 23:32:53.275 2000-09-21 (coding: 16# 3842 FE52 C554 03FF 0063 0000) Event 88 / 100: Event ID 16# 5371 Distributed I/0: End of synchronization of the number of distributed stations with the DP master/IO controller on slot 2: 1 Incoming event 23:32:53.258 2000-09-21 (Coding: 16# 5371 FF02 C150 0001 0000 0000) Event 89 / 100: Event ID 16# 4548 Entering STOP mode due to I/O management Previous mode: RUN request mode: STOP (internal) Internal error, incoming event 23:32:50.339 2000-09-21 (Coding: 16# 4548 FF84 C000 0000 8005 0000) Event 90 / 100: Event ID 16# 4302 Mode switched from STARTUP to RUN Startup information: - Timestamp time of last standby power-up - Current/last boot type for single processor operation: - Auto-warm restart admissibility for certain boot types after standby power-up: - Allow manual warm restart - Allow automatic warm restart The last valid operation or setting of the automatic start type on power-up: - After backup power-up, the operating mode before automatic warm restart: STARTUP (warm restart) requested operating mode: RUN entry event 05:13:04.808 2000-08-31 (Coding: 16# 4302 FF68 C700 0000 0810 7710) Event 91 / 100: Event ID 16# 1382 Request automatic warm start STOP Reason: STOP due to I/O management Boot information: - Boot without modified system configuration - No difference between default and actual configuration - Time stamp of last standby power-up - Single processor operation Current/last boot type: - Automatic warm restart after standby power-up Admissibility of certain boot types: - Allow Manual Warm Start - Allow automatic warm restart on power up The last valid operation or setting of the automatic start type: - OBs required for automatic warm restart after standby power up: Start OB (OB100) priority level: 27 Incoming event 05:13:04.806 2000-08-31 (Coding: 16# 1382 1B64 C772 4548 0810 7710) Event 92 / 100: Event ID 16# 4301 Mode switching from STOP to STARTUP STOP Reason: Startup information entering STOP mode due to I/O management: - Timestamp time of last standby power-up - Current/last boot type for single processor operation: - Auto-warm restart admissibility for certain boot types after standby power-up: - Allow manual warm restart - Allow automatic warm restart The last valid operation or setting of the automatic start type on power-up: - After backup power-up, the operating mode before automatic warm restart: STOP (internal) Requested operating mode: STARTUP (warm start) Incoming event 05:13:04.207 2000-08-31 (Coding: 16# 4301 FF46 C772 4548 0810 7710) Event 93 / 100: Event ID 16# 38C4 Distributed I/0: The station returns the address of the affected DP slave.: Station number: 99 DP master system ID: 1 Logical base address of the DP slave: Enter address: 1023 Logical base address of the DP master: 1022 Required OB: Rack failure OB (OB86) In the current operating mode, the OB was not found, or was disabled, or could not be started. External error, leaving event 05:13:03.809 2000-08-31 (Coding: 16# 38C4 FE56 C054 03FE 03FF 0163) Event 94 / 100: Event ID 16# 3842 Module determines the module type: Distributed I/0 input address: 1023 User information available Diagnostic interrupt from substitute OB required: Diagnostic interrupt OB (OB82) In the current operating mode, the OB was not found, or was disabled, or could not be started. External error, leaving event 05:13:03.733 2000-08-31 (coding: 16# 3842 FE52 C554 03FF 0063 0000) Event 95 / 100: Event ID 16# 5371 Distributed I/0: End of synchronization of the number of distributed stations with the DP master/IO controller on slot 2: 1 Incoming event 05:13:03.724 2000-08-31 (Coding: 16# 5371 FF02 C150 0001 0000 0000) Event 96 / 100: Event ID 16# 4300 Working mode before backup power on: Operating mode without voltage request: STOP (self-initialization) Incoming event 05:12:59.854 2000-08-31 (Coding: 16# 4300 FFF3 0000 0000 0000 0000) Event 97 / 100: Event ID 16# 494E Operating mode before power failure: STOP (internal) Requested operating mode: No voltage external error, incoming event 05:12:39.358 2000-08-31 (Coding: 16# 494E FF4F C000 0000 8005 0000) Event 98 / 100: Event ID 16# 39C4 Distributed I/0: Address of the DP slave affected by station failure: Station number: 99 DP master system ID: 1 Logical base address of the DP slave: Enter address: 1023 Logical base address of the DP master: 1022 Required OB: Rack failure OB (OB86) In the current operating mode, the OB is not found, or is disabled, or cannot be started. External error, incoming event 05:12:38.616 2000-08-31 (Coding: 16# 39C4 FE56 C054 03FE 03FF 0163) Event 99 / 100: Event ID 16# 38C4 Distributed I/0: The station returns the address of the affected DP slave.: Station number: 99 DP master system ID: 1 Logical base address of the DP slave: Enter address: 1023 Logical base address of the DP master: 1022 Required OB: Rack failure OB (OB86) In the current operating mode, the OB was not found, or was disabled, or could not be started. External error, leaving event 05:12:37.843 2000-08-31 (Coding: 16# 38C4 FE56 C054 03FE 03FF 0163) Event 100 / 100: Event ID 16# 3842 Module determines the module type: Distributed I/0 input address: 1023 User information available Diagnostic interrupt from substitute OB required: Diagnostic interrupt OB (OB82) In the current working mode, the OB is not found, or is disabled, or cannot be started. External error, leaving event 05:12:37.783 2000-08-31 (Coding: 16# 3842 FE52 C554 03FF 0063 0000) Can anyone help analyze whether it is a program or hardware reason?
Reply #22018-03-20
In the event of a fault, the CPU will automatically invoke the corresponding OB block to prevent the system from stopping; failure to invoke such a block or the absence of an appropriate block will result in the CPU ceasing to operate
Reply #32018-03-21
Analyze the causes of the failure? Is it a communication issue, a module problem, or an issue with the slave station connection cable?
Reply #42018-03-21
There is a fault with the DP slave station. On-site, the 300 CPU should be connected to the IM153 on the ET200M rack via its own Profibus interface. Check whether the SF indicator light on the IM153 is on First insert the tissue blocks OB82 and OB86, then install the lower part; this way your CPU won’t stop automatically. In the hardware configuration, set it to online mode and send a screenshot for me to see
Reply #52018-03-21
It is directly connected to PLC200 via a Profibus DP port.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.