There are 90 valves on site – how should one determine the capacity of the air storage tank, as well as the number and power of the air compressors? Please advise. V=Qv*T*P0/(P1-P2). What are the values of P1-P2?
Reply #22019-04-17
I’m not an instrument designer, so I don’t know much about it; it falls under the field of collection studies*.
Reply #32019-04-17
Following the standard design process, the gas consumption requirements of the instrumentation department are submitted to the mining and ventilation department, which then determines the amount of gas needed based on various data and regulations, including an overall estimate of the gas consumption required by the client in the future.
Reply #42019-04-17
P1 and P2 are the normal operating pressure and the minimum operating pressure, respectively.
Reply #52019-04-23
There is too much content to explain everything; take a look at sh3020-2013 and hg20509-2014 – the former is more detailed

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.