As the title suggests, when counting the IO points in a SIS system, is it necessary to have 1:1 redundancy for all types of points—AI/AO/DI/DO—and is this done to ensure that all cards are configured with redundancy? The SIL ratings are SIL1 and SIL2; this should have nothing to do with the actual SIL level, right? Is there any relevant standard that serves as a basis for this?
Reply #22019-07-05
In accordance with GBT 50770-2013 Code for Design of Safety Instrumented Systems in Petrochemical Industries, 5.0.14 states that redundant technology shall be employed for components such as the central processing unit, input/output units, communication units, and power supply units of logic controllers. As I understand it, if you are to follow this standard, then it should be redundant
Reply #32019-07-05
SIL2 level, redundancy is required
Reply #42019-07-08
This situation is relatively rare; once the SIL rating is clear, it’s sufficient to consult the relevant design institute. SIS generally requires triple or dual redundancy for the CPU; moreover, there is no need to use a SIS system for SIL1 levels, as DCS systems can meet the requirements of SIL1 on their own
Reply #52019-07-20
Generally, redundancy is used to improve safety and reliability. If it can be ensured that the SFF of the I/O cards is large enough, that’s also fine

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.