Will medium backflow show the flow rate?

2019-11-16View Original

Thread Content

The device is equipped with an orifice flow meter; if the medium flows in reverse, will the flow meter still indicate a flow rate? Please share your thoughts, thank you
Reply #22019-11-17
This issue should be divided into two parts; the first is related to the flow orifice plate. If there is a pressure difference on both sides, then fluid flow actually occurs. As for the flow direction, it relates to the installation orientation of the orifice plate; otherwise, the resulting pressure difference will vary depending on the direction. Secondly, as for what kind of measuring instrument to use, I won’t go into details; a relatively simple \"U\"-shaped tube will suffice to explain your problem. You might as well give it a try.
Reply #32019-11-17
In the case of backflow, the transmitter will display a negative differential pressure value. However, there is usually a minimum limit for this negative value, at -2.5 kPa (this is the case for Rosemount and Yokogawa transmitters in general). Generally, the flow rate displayed on a DCS should be 0. If the DCS is a newer version (the 700 system from Zhongkong), an ERR error message will be displayed
Reply #42019-11-18
It generally isn’t displayed; the pressure transmitter shows a positive value. If there are two pressure transmitters, it is possible to display the flow in the reverse direction as well. Some type of orifice flow meter can indicate flow in both forward and reverse directions

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.