Are shut-off valves allowed to be installed before and after the emergency cut-off valve?

2020-03-17View Original

Thread Content

Dear experts: Is it permissible to install stop valves before and after the emergency shut-off valve? Are there any relevant specifications?
Reply #22020-03-17
You can add it. Why can’t it be added? The emergency shut-off valve is a safety requirement, not an operational requirement. If your operation requires a stop valve, then of course it’s possible to use one. It’s just a question of whether it’s necessary. An emergency shut-off valve does not require an additional stop valve.
Reply #32020-03-17
Normative requirements stem from principles; as long as the principles hold true, it is possible to meet the norms. Additionally, your question should be about finding chemical engineering design codes or safety standards. Switch valves serve various purposes; for example, in a switching system consisting of a dozen or so such valves, automatic programming is used for control, and aside from the pressure equalization valve, no other shut-off valves are installed. For example, in the case of gas usage, one needs to be installed in front of the valve; there is no point in installing it behind the valve. Everything needs to be configured according to the process requirements.
Reply #42020-03-18
Personally, I don’t think it’s a matter of spending money; when it’s not possible to operate it, this valve is still very necessary!
Reply #52020-03-18
If the emergency shut-off valve needs to be serviced during production, what should be done since there are no stop valves at either the front or back?
Reply #62020-03-19
This post was last edited by nestorsong on 2020-3-19 at 18:15. I hope it will be helpful for your work. GB26980-2011 Standards for fuel filling systems of liquefied natural gas vehicles; GBT 20368-2012 Production, storage and transportation of liquefied natural gas (LNG); HG_T 21608-2012 Technical requirements for liquid loading and unloading arms
Reply #72020-03-24
It can be added; it is generally used for the repair or replacement of control valves

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.