I can’t figure out the program for setting a delay timer on an S7-300 PLC

2020-04-04View Original

Thread Content

I can’t understand the program for activating a delay timer on an S7-300 PLC. As shown in the diagram, why doesn’t T0 get activated at any point? It keeps timing continuously, in a cyclic manner; I really don’t understand this program
Reply #22020-04-05
From your program, it seems that timing is continuous; once 5 seconds have passed, the timer turns on for just one scanning cycle before turning off, and then timing starts again
Reply #32020-04-05
The 3rd floor is correct. Your approach with the timer is to turn it on when the set time expires, and then use the pin that activates the timer to turn it off again, thereby resetting the timer.
Reply #42020-04-06
It seems I understand now – the location where the timer is located cannot have things turned on at the same time; it can only set a timer repeatedly, which is why setting a value later also has no effect: handshake

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.