2020-06-30View Original

Thread Content

Could any experienced engineer provide some guidance? When calibrating the Rosemount 3051RES, the 475 handheld device cannot locate the transmitter on the low-pressure side, and the DCS is unable to read the differential pressure value.
Reply #22020-06-30
Check the wiring directly; the A and B terminals of the master and slave instruments are connected in a cross pattern, not in parallel
Reply #32020-07-02
Thank you for the reply from the second floor; the wiring on site was correct and the problem has been resolved. Let me share our experience in handling this: use a manual controller to switch between the high-voltage and low-voltage sides, then switch back, and the device will be found. This is also a troubleshooting method provided in the 3051ERS user manual.
Reply #42020-07-14
Great majors on the second floor. First, checking the wiring is correct; AB is easy to get mixed up. If the wiring is fine, then it will be more troublesome

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.