What to do if there is no grounding when using an electromagnetic flowmeter in an office building?

2020-08-23View Original

Thread Content

A water circulation system was installed in the office building, using PVC pipes; however, there is no dedicated grounding point – only the ground wire from the three-prong outlet on the wall. After connecting it, the readings fluctuate greatly. What can be done to solve this issue? It’s on the 6th floor, and a grounding wire has been connected there for controlling the water pump with an inverter. 269
Reply #22020-08-23
From the picture, it seems that your flow meter has a grounding ring; try connecting this grounding ring directly to the metal water pipe as a ground wire
Reply #32020-08-23
Check if there is a equipotential bonding box in your room. If so, it has grounding terminals inside. Furthermore, PVC pipes are non-conductive; therefore, the flowmeter body and the grounding ring need to be connected together and grounded as a single unit.
Reply #42020-08-23
Some flowmeters are virtually grounded and do not require a ground wire. If the flow rate remains stable without grounding here, then it’s not necessary to ground it; after all, it’s just water, so there’s no need to worry about static electricity buildup. (If powered by 220V AC, the enclosure must be connected to the ground for protection.)
Reply #52020-08-23
Logically, Yokogawa’s electromagnetic flowmeters should be quite stable; the fluctuation range at the moment is simply too excessive
Reply #62020-08-23
There are many reasons for significant fluctuations in values; it’s best to check whether your pipeline pump is operating smoothly and whether there is any vibration.
Reply #72020-08-24
What is the function of this flow meter?
Reply #82020-08-24
The most experimental approach is to circulate the water
Reply #92020-08-25
The instrument ground and the power ground should not be connected together on the upper floor; it is better to use metal pipes for connection.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.