The positioner was working normally before, but it suddenly stopped functioning. The issue is that it doesn’t respond to signals; it can be switched to full open or full closed manually. There are no problems with the air supply or the signals, and the pilot valve is also fine. I’d like to know what’s causing this problem
Reply #22021-01-07
First, try moving the nozzle baffle manually to see if it moves; giving a signal manually on-site will let you know
Reply #32021-01-07
The nozzle baffle moves, but no signal is generated locally; no action is taken
Reply #42021-01-08
Check the electromagnetic coil section to see if there are any changes in the signal and current. If the manual damper functions properly, it indicates that there are no issues with the valve or the gas supply system
Reply #52021-01-08
Has the locator been subjected to a self-check or manual calibration? Try again after the calibration is complete; if it still doesn’t work, it’s possible that the circuit board of the locator is damaged.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.