The alarm signal for levels below 4MA at the site is cleared

2021-09-06View Original

Thread Content

Some of the instrument signals at the site are below the 4MA alarm level; how can these alarms be eliminated?
Reply #22021-09-06
It is an alarm from the control room DCS due to the field instrument signal being below 4 mA; Is it still the case that the field instrument reads below 4mA, triggering an alarm on the instrument’s display?
Reply #32021-09-06
When the field instrument signal is below 4 MA, it is a DCS alarm.
Reply #42021-09-08
Values below 4 mA can be displayed as 0, which helps to prevent unnecessary alarms in the DCS
Reply #52021-09-12
The alarm at levels below 4 mA occurs because the default configuration for the bottom section is usually between -5% and 105%. It is possible to set the minimum value in the DCS configuration to 0%, rather than -5%, so as to prevent low values from appearing during DCS signal conversion. It is also possible to change the value in the HART communication settings field at the table header to 0%, or to a slightly higher value of 1%–2%; in that case, the output from the circuit board will not be low
Reply #62021-09-12
This post was last edited by jlshnlhj on 2021-9-13 at 11:57. Correction: The alarm for values below 4mA is an IOP alarm; when the setting is 0%, it indicates an alarm for values below 4mA. -5% corresponds to values below 3.2mA, -10% corresponds to values below 2.4mA, and the lowest value is -25%. If alarms are triggered frequently, the 0th bit should be low; if it is within the error range, the lower limit can be set to -10% or -15%.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.