Flammable gas alarm

2023-07-17View Original

Thread Content

Dear sea friends: There are 16 combustible gas detectors, 8 of which were installed later. After installation, the signals from 3 of these detectors could not be transmitted to the main unit. Please help analyze the reason for this. 1. The wiring sequence of the combustible gas alarm is correct ; 2. The combustible gas alarm is in good condition. 3. The line test is normal. Thank you.
Reply #22023-07-17
Is it communication that carries the signal from the alarm to the host?
Reply #32023-07-17
Determine whether it is 485 or 4-20 milliamps. If it is 485 communication, pay attention to the dialing address as well as the installation location; also consider the installation length, and check whether the power supply has sufficient capacity
Reply #42023-07-17
Based on the information you provided, the possibilities of an incorrect wiring sequence for the combustible gas alarm, damage to the alarm itself, or abnormal wiring tests have been ruled out. The possible reasons are as follows: 1. Excessive signal transmission distance: The signal transmission range of combustible gas detectors is limited; if the detector is installed too far away from the main unit, it may not be possible for the signal to reach the main unit. You can check whether these faulty alarms are located far away from the main unit. 2. Signal interference: If other electronic devices or power lines are located near these alarms, it may cause signal interference, preventing the signals from being transmitted to the main unit. You can check whether there are any other electronic devices or power cables around the alarm, and try to avoid interference as much as possible. 3. Signal line failure: Although you state that the line test was successful, there may still be issues such as loose or broken connections in the lines. You can check whether the signal wires of these faulty alarms are firmly connected, with no damage or looseness. If the above methods do not resolve the issue, it is recommended that you contact a professional for further inspection and repair. .
Reply #52023-07-21
With the 485 bus, it’s very likely that the signal is diffraction; add matching resistors

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.