Are there any requirements for the cofferdam in the methanol washing zone?

2019-06-12View Original

Thread Content

Are there any requirements for the cofferdam in the methanol washing boundary zone? There are requirements for cofferdams around storage tanks; are there any requirements for the plant area as well?
Reply #22019-06-12
\"Code for Fire Protection Design of Petrochemical Enterprises\" (GB50160-2008) (2018 edition), 5.2.28: Around equipment areas where there is a risk of leakage or spillage of flammable liquids during startup, shutdown, or maintenance operations, dikes and liquid diversion facilities with a height of not less than 150 mm shall be installed.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.