Must accident exhaust fans be installed in high and low voltage substations?

2019-03-01View Original

Thread Content

\"GB50053-2013 Code for Design of Substations of 20 kV and Below\", 6.3 Heating and Ventilation: Transformer rooms and distribution rooms should make use of natural ventilation; when natural ventilation is insufficient, mechanical ventilation should be installed. Are there any mandatory fire safety requirements that dictate the installation of accident exhaust fans?
Reply #22019-03-01
According to the fire safety inspection, it is necessary to install accident exhaust fans
Reply #32019-03-02
Could you please specify which fire safety regulation it is? Thank you!
Reply #42019-09-10
\"DLT 5725-2015 Code for Construction of Substations for Power Users at 35 kV and Below\", 15.4.1.2 The distribution equipment shall be equipped with emergency exhaust fans that can provide at least 10 air changes per hour; such fans can also be used for normal ventilation purposes.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.