Cable 10S can withstand a maximum current

2019-03-07View Original

Thread Content

This post was last edited by sdscj0122 on 2019-3-8 09:20. For a 185-square-millimeter cable connection, is it possible to start a 1MW asynchronous generator? There is soft starting, and normal operation ensures that the current is kept at 600A. What’s a concern now is whether the cable can withstand the stresses during startup I hope everyone here can help out, thank you! PS: For a 185 dual-unit unit, a normal rating of around 900A should be fine.
Reply #22019-03-08
A 1MW motor means 1000kW; it is definitely powered at 10kV voltage. The rated current of the motor is about 57A – so it must be a 10MW motor, right? The three-core 10kV, 185 square millimeter cable has a rated load current of 410 amps at an ambient temperature of 25 degrees; when two such cables are used together, the current capacity rises to 820 amps. By applying various coefficients, it can handle a current of around 600 amps, which is sufficient to meet the rated operating current requirements. It takes a few seconds to over ten seconds to start up, and there is no problem with withstanding the starting current for a short period of time.
Reply #32019-03-08
It’s powered by 380V, wooh!
Reply #42019-03-08
The motor has a power of 1 MW and is powered at 380 V; its rated current is around 1520 A. Using cables with a cross-sectional area of 185 square millimeters is simply not sufficient for such requirements. It’s unbelievable that a motor with a power of 1000 KW operates at 380 V – and no one has ever mentioned this before

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.