Can cable trays be installed above steam pipes?

2019-03-10View Original

Thread Content

We have three layers of conduit racks: the steam pipes are on the second layer, and the cable trays are on the third layer. The distance between each layer is 1.75 meters. According to the design specifications, this arrangement is not acceptable, as cable trays cannot be placed above steam pipes. Are there any regulatory requirements regarding this?
Reply #22019-03-10
According to clause 5.1.7 of GB50217-2018, the \"Design Standard for Cables in Electrical Engineering\", which states that \"cables installed openly should not be laid parallel above thermal pipelines\", it seems that this is not allowed
Reply #32019-03-10
It seems that regulations already exist! Does anyone know why?
Reply #42019-03-11
The steam pipes generate heat, and the rising hot air causes the cables to heat up, which is not good for them
Reply #52019-03-15
Cable trays should be kept away from heat sources, as well as power cables

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.