True or False question: Please answer whether it is correct or incorrect. 3 points for a correct answer, 2 points for an incorrect answer, and 5 points for a detailed explanation of the reason. When a cable-type zero-sequence current transformer is used for grounding protection, the grounding wire at the cable terminal must be passed through the core hole of the zero-sequence current transformer before being grounded.
Reply #22020-03-09
Error. When the cable grounding point is below the zero-sequence current transformer, the ground wire should be grounded directly ; When the grounding point is above the zero-sequence current transformer, the grounding wire should pass through the zero-sequence current transformer for grounding. At the same time, the metal shielding layer and grounding wire of the cable segment from the cable terminal to the zero-sequence current transformer should be insulated from ground, with an insulation resistance to ground of not less than 50 kΩ.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.