HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Unstable PLC current input

2015-07-03View Original

Thread Content

For Siemens PLC analog inputs, the field device provides a 4-20mA output from a mass flow meter; when the flow rate is 0, the PLC shows fluctuations between 0 and 4 mA. A 4–20mA signal sent from a signal generator on-site shows normal operation. Once connected to the instrument, the display becomes abnormal, with unstable fluctuations.
Reply #22015-07-03
Modify the PLC configuration to remove the signal below 4mA. Check whether the supply voltage for the mass flow rate is normal? Is it suspected that the PLC card does not have sufficient load-bearing capacity? Or is the impedance of the mass flow meter too high? For current-source type signals, the lower the instrument impedance, the better.
Reply #32015-07-03
A 4–20mA signal was sent to the field using a signal generator, and the display showed normal operation; therefore, there is an issue with the output of the mass flow meter. The output circuit of the flow meter was checked, and if it could not be repaired, a new one was installed.
Reply #42015-07-03
It seems there’s still a problem with the mass flow meter; let’s try another one
Reply #52015-07-03
What does this have to do with PLCs? The signal isn’t provided by the PLC

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.