Thread Content
As the title suggests, how can the Fisher locator be changed to a reactive mode? Solve
It has not been used; if there is no reverse action switch on the locator, the reverse action setting of the regulator can be changed, and this will also enable the locator to output in the opposite direction.
You can just make the changes on your DCS; it has functions like inverting signals, and the effect is the same as that of reversing the reaction from a locator. I’m not sure what system you’re using
Well, it can be changed inside, but I want to know how to make changes on the locator side
Are you referring to the Fisher6200? The communication frequency of 475 can be changed. The manual seems not to allow it to be shared. For the general settings within 475, go to Device Settings; select “Out in Service”. Choose the pressure unit, the type of amplifier, and the travel control options. For the actuator manufacturer, select Fisher. Choose the actuator model based on the information on its label, and enter the actuator’s size and model according to the details on its label. This is where the option for forward or reverse operation comes in – choose whether the valve should stay open or closed depending on the conditions. There are a few more options, but I won’t go into detail about them
Uh, is there a manual? That option selected the reaction option, but it seems like nothing has changed. Could you send me a manual?
Is it enough to just change this here? Is no other adjustment needed?
The instructions are too large; 5M doesn’t allow their transmission. Previous steps cannot be skipped; a choice must be made
Well, can you send it to my email? 582794315@qq.com Thank you!
It has been sent; I hope it will be helpful to you
In the instrument, within the analog input range, simply reverse the range of the analog signal input. You can give it a try