2015-08-27View Original

Thread Content

We are a storage facility for liquid chemical products. Following the explosion at Tianjin Port, we, as expected, once again faced a series of safety inspections by officials at all levels. After an inspection by a higher-level inspection team in our reservoir area, they raised an issue regarding the clear height of the pipe racks passing through that area. We designed the pipe rack in our reservoir area to have a clear height of 4.5 meters above the fire exit, and it was approved during the fire safety inspection at that time. However, the inspection team stated that the clear height of the pipe rack must be at least 5 meters, citing fire safety regulations. I would like to ask everyone: is it really stipulated by the regulations in this way? What regulations require it? Note: If changes are to be made, all the pipe racks in our storage area will need to be modified. These dozens of pipe racks are associated with numerous process pipelines, and as a result, operations will almost come to a standstill.
Reply #22015-08-27
No reply. . . . . Is this question very obscure? Push it yourself
Reply #32015-08-27
Fire safety regulations – I’m not very familiar with these; they should be considered **laws and regulations**
Reply #42015-08-27
Theoretically, such problems should not occur, as the relevant laws and regulations were surely taken fully into account when formulating the standards. However, if the standards require higher levels of compliance, that becomes more complicated. I’m not sure what the regulations stipulate regarding existing facilities !
Reply #52015-08-27
Thinking back, 5 meters and 4.5 meters seem to be the distinctions between main roads and secondary roads; the original poster might want to take a look
Reply #62015-08-27
I don’t know what the standard is? Could you provide it?
Reply #72015-08-27
Check the minimum height for fire trucks to pass. . I guess the Fire Protection Law isn’t that clear – it must be 5 meters, right?
Reply #82015-08-27
According to Article 9.1.6 of the latest design codes for oil storage tanks: when crossing fire roads, the clearance height should be no less than 5 m; when crossing other vehicle roads, the clearance height should be no less than 4.5 m. Now, liquid chemical storage facilities are governed by the petroleum storage design codes.
Reply #92015-08-28
Xiao Li, the height limit for road overpasses should be uniformly set at 4.5 meters. In the event of an accident, in addition to using one’s own fire trucks for firefighting and rescue operations, external fire departments must be called upon in certain situations. To reach the scene by road, the vehicle height must not exceed 4.5 meters

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.