Reasons for the frequent failure of ion exchange columns in thermoelectric steam chemical dosing system analyzers

2015-09-07View Original

Thread Content

We maintain online analyzers for thermoelectric steam chemical dosing systems. The ion exchange column resin used in the pre-treatment of online analyzers needs to be replaced once a week; otherwise, the conductivity will be too high. The frequency is too high, resulting in a large workload. I would like to ask the experts in chemical analysis to help identify what is causing this issue and find a solution. Thank you first!
Reply #22015-09-08
The reasons are one or more of the following: 1. Insufficient purity of the water treated upstream, with a high amount of ionic impurities remaining in the water; 2. The capacity of the ion exchange resin columns or beds is too low; 3. Improper packing of the ion exchange resin columns or beds, resulting in channeling; 4. Significant seepage and leakage from the pipes and containers in contact with the water, causing contamination
Reply #32015-09-09
Thank you, so much thanks:D:D:D:D:D:D:D:D:D

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.