What is the most basic measure to prevent static electricity fires when transporting flammable liquids through pipelines?
It involves adding static grounding to the pipelines; if necessary, static bonding is required between the flanges.
Control the flow rate, discharge static electricity, and add bypass connections
(1) Strictly control the flow rate of the liquid in the pipeline to keep it below the limit flow rate; (2) Install a grounding device that meets the standards.
Additional note: The conductivity of the oil should be greater than 50; if this requirement is not met, an antistatic agent should be added
Control the flow rate and ensure proper grounding; the flanges should be electrically bonded.
What is the most basic measure to prevent static electricity-induced fires when transporting flammable liquids through pipelines? The static grounding measures for pipelines, various ones
Static grounding, flange bonding. ---------------------------------------------------
I agree with the above statement,,,
1. Keep the flow rate below the electrostatic safety flow rate; 2. Static grounding should be provided at intervals along the pipeline at regular intervals ; 3. The flange is used for static electricity bonding ; 4. Connect to ships and similar vessels that may generate a potential difference, and install insulating flanges.
Strictly control the flow rate, and check the grounding at all locations, including pumps, pipelines, flange connections, etc.