For 4-20 mA signals sent to a DCS, what is the typical threshold below which it is considered that there is no signal at the field level?
Reply #22015-10-27
It should be below 3.7mA. . . .
Reply #32015-10-27
There is some volatility at zero point, so it’s normal for the value to be below 4 Ma sometimes; here it’s 3.8 Ma
Reply #42015-10-27
It depends on one’s own settings; to eliminate the impact of gauge errors, setting it around 3.5mA is sufficient.
Reply #52015-10-27
No signal means below 4mA, and a signal of zero means 4mA. When the 4~20mA standard was established, this concern of the original poster was taken into account, which is why the zero point was set at 4mA.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.