Is the pressure switch connected to the DCS?

2015-11-23View Original

Thread Content

1. Is a relay isolation required when connecting an explosion-proof pressure switch to a DCS? 2. Is a intrinsically safe pressure switch requiring connection to a DCS needs to be isolated by a safety barrier?
Reply #22015-11-23
I didn’t pay attention to whether there is a difference between explosion-proof and intrinsically safe types for pressure switches; generally, using a relay for isolation is sufficient.
Reply #32015-11-25
Are there intrinsically safe pressure switches? All those available currently have an external 220V power supply, so they cannot be made intrinsically safe
Reply #42015-11-27
Does a pressure switch require power? I’ve never seen that. It doesn’t matter whether the pressure switch is used or not
Reply #52015-11-29
It seems I haven’t seen a pressure switch for power supply yet. Do you have any samples? Shared hash
Reply #62015-11-29
Who can answer me? Under normal circumstances, is the pressure switch connected directly to the DI card or DI safety barrier as a dry contact? What is the relay supposed to do? For example, with the solenoid valve at the DO point, it is the DO card that needs to control the solenoid valve through a relay, right?
Reply #72015-11-29
A pressure switch is generally just a dry contact connected to the DCS; it seems that safety barriers are used less often in this context
Reply #82015-11-30
If the pressure switch is a purely mechanical switch (such as a microswitch). 1. If a intrinsically safe circuit is designed with a DI safety barrier, this meets the requirements for intrinsically safe explosion protection. 2. If it is designed as a \"non-intrinsic safety\" circuit, the relay provides isolation; handle it according to your design practices. 3. DO represents the load, which are field devices such as solenoid valves; therefore, DO is a power output. It is advisable to use DO relays for isolation in order to prevent short circuits at the field level, which could cause high currents and damage the DO channels. A mechanical switch, since it has no energy storage components inside (such as inductors or capacitors), does not require an intrinsically safe certificate; a safety barrier is sufficient to create an intrinsically safe circuit. You can design it as an “intrinsically safe” or “non-intrinsically safe” circuit (such as flameproof) based on the overall requirements of the project. It is beneficial to add an isolation layer to the entry and exit signals at the site, whether it’s a safety barrier/isolator/relay. Keep the enemy out of the country’s borders. @jiaguoyun
Reply #92015-11-30
1. The flameproof pressure switch is connected to the DCS; no intermediate relay is required – it can be connected directly to the card slot. 2. Intrinsic safety pressure switches are connected to the DCS; all intrinsic safety instruments must be equipped with safety barriers, otherwise they cannot form an intrinsic safety circuit, and such instruments lose their intrinsic safety significance and function.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.