Distillation kettle level selection

2015-12-10View Original

Thread Content

The existing distillation vessel has a capacity of 2000 liters; it operates under negative pressure, with a distillation temperature of 70°C. The residual material is quite viscous at the end, and there is no mist inside the vessel during the distillation process; Current analysis: Double flanges cannot be used due to crystallization ; The float ball cannot be used; there is stirring inside it ; Ultrasonic waves cannot be used because of the negative pressure ; The radar cannot be used; the detection probe is too close to the tank wall ; Seeking advice from fellow sea lovers
Reply #22015-12-10
Since there is no mist inside the tank during the distillation process, it is not necessary to install a level gauge; it can be checked directly. (Haha, do the opposite)
Reply #32015-12-11
Thank you to those who replied; none of these methods work, and I hope everyone will continue to participate
Reply #42015-12-11
It can be used with radar, E+H models, even on small 100L kettles
Reply #52015-12-12
The method suggested upstairs is good. The problem is that there are approximately 7–8 process pipes on the boiler; should all of them be replaced with flexible connections? Additionally, due to continuous feeding, does the expert upstairs have any other good suggestions?
Reply #62015-12-17
It seems there is a problem with my description; determining how to use a pivot point is a rather tricky issue, as crystals will form after distillation for a certain period of time. I would like to ask for further advice
Reply #72015-12-17
Actually, the claim that the radar mentioned by the original poster doesn’t work is a bit absolute; it seems the poster hasn’t conducted any tests. I guess it’s actually possible to use radar for that
Reply #82015-12-18
Reactor vessels are usually equipped with weighing functions; you can consider this aspect
Reply #92015-12-18
For guided-wave radar level gauges, the rod-type version should work fine; as long as the tank wall is smooth and flat, with no additional instruments installed on it or any other obstacles, a distance of 50 mm is sufficient. We use this type of gauge regularly, and it works well even with viscous fluids – we have also used it for asphalt

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.