2016-03-07View Original

Thread Content

For Siemens single-acting positioners, the valve position should be fully closed when the input is at its minimum value; yet the displayed valve position is 20% – why can’t it reach 0? How to fix this? ?
Reply #22016-03-07
There are too many Siemens positioners; what are the models? Generally speaking, mechanical types require zero adjustment, while electronic types require self-tuning.
Reply #32016-03-07
Try using self-tuning without considering the limit setting
Reply #42016-03-07
It should be the pressure release valve, right? Check what the output is; if it’s not due to a limit issue or a stuck valve, self-tuning usually solves the problem.
Reply #52016-03-08
Recheck it; the possible reasons are: 1. Blockage in the air circuit inside the locator, 2. The feedback rod is loose or installed in an incorrect position

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.