2016-03-18View Original

Thread Content

The two faulty Rosemount pressure transmitters were repaired by the manufacturer; after being installed yesterday, their ranges were adjusted using Hart software. One of them was adjusted successfully, while for the other, access to display settings was restricted after connection. I seek guidance from all the experts out there.
Reply #22016-03-18
What model is it, and is it write-protected? Could you send the text from the image in the hint?
Reply #32016-03-18
It seems there’s a write protection jumper on it; please check the transmitter’s manual in detail
Reply #42016-03-22
There should be jumpers; I encountered this once before, where it was necessary to adjust the jumpers inside the meter.
Reply #52016-03-26
First look at the jumper, then the dd version. It’s possible that the transmitter has been upgraded while your controller version is outdated.
Reply #62016-04-02
Are you using the genuine 375 or 475? Some domestically produced devices may encounter such problems

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.