Question about question 28 on the morning of the first day of the 2011 exam for the relevant major

2016-05-29View Original

Thread Content

28. For a heat exchanger with a water flow rate of 590 m/s, an inlet water temperature of 20°C, and a heat transfer rate of 3.5×104 kJ/s, given that the specific heat capacity of water is 4.1868 kJ/(kg•°C) and no heat losses are considered, what is the outlet water temperature in °C? Choose from the options below A、40 B、35 C、45 D、34. Something seems wrong with this water flow rate
Reply #22016-05-29
The flow rate unit is m/s, there must be a problem
Reply #32016-05-30
The mass flow rate of D should be in kg/s; 590*4.1868 (T-20) = 35000, T=34C

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.