The pressure transmitter suddenly shows the maximum range

2016-06-13View Original

Thread Content

During normal operation, the pressure transmitter suddenly shows the maximum range value. The pressure tapping valve was closed and the system was emptied, but the indicator still shows the maximum range value. Could experts help analyze what could be the cause? A new transmitter has been installed and it shows normal readings; it seems the original transmitter was damaged
Reply #22016-06-13
If the transmitter diaphragm box undergoes irreversible deformation, it is damaged
Reply #32016-06-13
If it shows the maximum value even when there is no pressure, it indicates that the pressure transmitter is damaged and needs to be replaced.
Reply #42016-06-13
It occurs frequently in winter due to freezing, but is rare in summer
Reply #52016-06-14
The diaphragm is damaged; as for the cause of the damage, the original poster needs to analyze it in conjunction with the operating conditions

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.